    Carrier Blower Issue (3 Posts)

  • JamieP JamieP @ 8:56 AM
    Contact this user

    Carrier Blower Issue

    I have a Carrier 58VLR105---11112 low boy oil fired furnace with a variable speed blower.
    The green LED light on G is illuminated but the blower is not running.
    How do I determine if it is a bad blower, harness, or board.
    There is 120 Volt at the motor
  • JStar JStar @ 9:37 AM
    Contact this user

    Blower

    You should check the capacitor first, then ohm out the motor to check for continuity, open circuits, or grounding.
    - Joe Starosielec
    http://thatcherhvac
    http://facebook.com/thatcherhvac



    Guaranteed performance. Guaranteed energy savings.


    Serving all of NJ, NYC, Southern NY State, and eastern PA.

    Consultation anywhere.

    (Formerly "ecuacool")
  • unclejohn unclejohn @ 10:57 PM
    Contact this user

    That motor

    Dosent have a run cap. Don't think those VS oil burners have been out that long it may still be under warranty. Call Carrier direct to find out, just give them ser.# at 1800carrier.probley just the controller is bad and not the motor. If its still under warrant have them replace both.
  •  