    condensation

    What would cause condensation on the Pvc condensate drain on a air handler...? Thanks Paul S
  • alotlikeearl alotlikeearl @ 10:26 AM
    Contact this user

    Humidity

    Cold water inside drain and hot humid air on the outside. 
  • Paul S Paul S @ 11:09 AM
    Contact this user

    humid

    how do you solve that problem if it didn't happen with the system before?...thanks Paul S
  • RJ RJ @ 2:31 PM
    Contact this user

    condensation

    Any time you are operating a DX or chillwater coil you will have some condensate if the unit is operating correctly and there is moisture present in the air stream,  the higher the relative humidity the more condensate.  check your cond. drain line and trap and flush them out if needed, make sure your trap and condensate piping are installed per unit recommendations.
    RJ
  • alotlikeearl alotlikeearl @ 3:44 PM
    Contact this user

    Insulate

    Insulate the drain line with Armaflex as you would a suction line.
  • Paul S Paul S @ 9:18 PM
    Contact this user

    condensation

    Thanks guys....Paul S
  • Eugene Silberstein Eugene Silberstein @ 10:32 AM
    Contact this user

    Best Practice

    It is best practice to insulate the condensate drain line for a minimum of ten feet to help eliminate the condensation issues.
    Eugene
  •  