The Wall
Forum / Oil Heating / Beckett AFG Stalls
  • Post a Reply to this Thread
    Beckett AFG Stalls (7 Posts)
  • vega vega @ 5:08 PM
    Contact this user
    Beckett AFG Stalls
    Boiler fires right up , but stalls within about one minute. It was turned 10 months ago, even the  electrodes were changed.  But to be on the safe side , I  cleaned boiler, Changed filter, strainer and cad photo cell , Fuel lines were blown clean , fuel is bright pink. It fires up each time but won't remain on
  • Steamhead Steamhead @ 7:54 PM
    Contact this user
    If you had to clean it out after 10 months
    it wasn't set up properly to begin with, You need a pro to fix this, but not the one that was there last time. Try the Find a Contractor page of this site.
  • vega vega @ 9:35 AM
    Contact this user
    Beckett AFG Stalls
    Actually it didn't need to  be clean , since I was trouble shooting I figured I might as well vacuum it , there was no soot build up .It was the cleanest it's ever been. The nozzle , the strainer and filter were all in very good condition, none of them needed to be changed , I just thought if I was taken it a part I would changed everything that was easy to get too. I didn't want to make 4 trips to the store. Thanks for reading my post and replying to my situation
  • JStar JStar @ 5:49 PM
    Contact this user
    Oil
    What were the combustion numbers?
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac
    http://facebook.com/thatcherhvac
    Guaranteed performance. Guaranteed energy savings.
    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    (Formerly "ecuacool")
  • Alan Welch Alan Welch @ 6:35 AM
    Contact this user
    Stalls ?
    A car stalls. Not an oil burner.  Are you having to push the reset every minute? or is the burner sputtering due to fuel supply issues (underground tank ? )  sounds like you need a good technician to troubleshoot , or we need more info  to help you diagnose.
  • Jim Davis Jim Davis @ 10:11 AM
    Contact this user
    burner shutting down
    If you have a 2-line system the problem is simple, you are losing prime.  If that is a newer burner with the interrupted spark I would expect this to happen.  I don't recommend either one.  Need to go to single line or constant(intermiitent)  spark.
  • Ed N.Y.C. Ed N.Y.C. @ 1:41 PM
    Contact this user
    stalls
    oil is bright pink ? sounds like h2o in oil.should be red  ED N.Y.C.