    Is a Chimney Liner necessary with a Gas Power Burner?

    Hi- Is a chimney liner required when you install a wet based boiler (or convert one from oil) with a gas power burner?
    Thanks!
    - Rod
  • Danny Scully Danny Scully @ 6:03 PM
    Contact this user

    I believe

    I believe so. It certainly is in Nassau County, NY. The flue gas temperature is still reduced as it would be from a conventional oil to gas conversion, causing condensation in the chimney. Without a SS liner, the chimney could deteriorate. The only exemption I've used before is if the chimney runs through the interior of the house only.
  • Charlie from wmass Charlie from wmass @ 8:56 AM
    Contact this user

    It depends

    Mass code says it is not required unless conditions warrant it. I recommend doing it as a general thing due to the lower flue temps Like Danny mentioned.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
  • Rod Rod @ 10:07 AM
    Contact this user

    Chimney Liner with Gas Forced Draft

    Thanks guys for your responses. It would seem to me that most of the applicable codes are written with an atmospheric system in mind and I was just wondering whether having a forced draft made a difference.
    - Rod
  • Charlie from wmass Charlie from wmass @ 9:36 PM
    Contact this user

    Yes it is different with forced draft

    If you look at the charts for chimney size it is smaller for forced draft for the same given btu rating of boiler.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
  • Aus Aus @ 1:08 PM
    Contact this user

    Stainless steel versus aluminum

    Will an aluminum liner suffice OR is stainless steel the only way to go?
  • Rod Rod @ 3:07 PM
    Contact this user

    Aluminum Chimney Liners.

    Hi- I would definitely go with stainless steel. I'm not sure why they even have aluminum liners as aluminum corrodes almost if you look at it wrong.  There are also different qualities of stainless steel used for liners. In stainless steel liners, I'm not sure how much actual benefit one would get using a more premium quality over regular 304.
    - Rod
  • bob young bob young @ 11:23 PM
    Contact this user

    LINER

    MAKE SURE YOU DON'T GET ROBBED. LOTS OF UNSCRUPULOUS  CHIMNEY GUYS AROUND. GET A FEW QUOTES.   bob nyc lic. plbr
  • Dave in QCA Dave in QCA @ 10:11 AM
    Contact this user

    Tile liner?

    On our system, the original 1909 chimney is located on the interior of the house and does build up a little heat.  The chimney is lined with tile.  The boiler(s) have been fired on natural gas since 1954 and there does not appear to be any detioration.  I have to note though, that the old Pennco really kept the chimney hot, and the surrounding walls stayed quite noticeably warm.  The new WM-680 with Riello burner, running on low fire does not make the chimney hot.  There is a little noticeable warmth, but not much. 
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • SWEI SWEI @ 11:13 AM
    Contact this user

    Running on low fire does not make the chimney hot

    Might be interesting to know the flue temp in the top third or so of the chimney.
  • Dave in QCA Dave in QCA @ 11:29 AM
    Contact this user

    3rd floor

    The highest point I can touch the chimney is at the 3rd floor level.  The finished all at that point is plaster directly on the chimney.  Warmth can still be detected but not near as much as with the old boiler.  The lower temperatures seem to consistent no matter where you are checking.
    Of course, the old boiler was an atmospheric with no flue damper.  When it was running it had pretty high flue temps and when it was not, there was still a huge draft throught the boiler and up the chimney.  The new boiler runs with lower flue temperatures and the new power burner has a little inlet damper that completely closes when the burner shuts down.  So, the off time flow of heat up the chimney is reduced to near zero.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • Tim McElwain Tim McElwain @ 7:38 PM
    Contact this user

    ANSI 21.8 Installation of Domestic Gas Burners since

    2002 requires the chimney to be lined.
  • bob young bob young @ 7:58 PM
    Contact this user

    TIM rules

    the man has spoken. listen to him. i for one ALWAYS do !!  bob nyc lic. plbr
  •  