Forum / Strictly Steam / Testing & setting presuretrol
  • Post a Reply to this Thread

    Testing & setting presuretrol (4 Posts)

  • gcp13 gcp13 @ 8:18 AM
    Contact this user

    Testing & setting presuretrol

    I made this device to test presuretrols and recalibrate
    Them by adjusting the set screw until I get what I need
    Leaving the fittings loose on tester lets the presure drop slowly
    After it trips to see when it closes.
    Works very well. I've had new presuretrols out of the box
    Not shut off until 7 lbs. while it was set to 1lb.
  • BobC BobC @ 1:57 PM
    Contact this user

    great idea

    Honeywell should be embarrassed into doing something about this but because they have a monopoly they just continue to ship crap.It's a crime that they don't have any competition.

    Bob
    Smith G8-3 with EZ Gas @76,700 BTU, Single pipe steam


    Vaporstat with a 12oz cut-out and 4oz cut-in


    3PSI gauge
  • Dan Holohan Dan Holohan @ 2:55 PM
    Contact this user

    Great idea.

    Thanks for sharing. Seems a shame you have to do this on a brand-new product.
    Site Administrator
    dan@heatinghelp.com













    Hug your kids.
  • gerry gill gerry gill @ 10:04 PM
    Contact this user

    Nice rig,

    i like it..yea we play with the calibration screw also..i think the first person laid off at honeywell at the start of the recession was the qa inspector.