Forum / Oil Heating / Another Burnham V7 question
  • Post a Reply to this Thread

    Another Burnham V7 question (3 Posts)

  • bill bill @ 12:40 PM
    Contact this user

    Another Burnham V7 question

    Well last winter I had a V7 with a cracked heat exchanger. I posted the issue here and received quite a bit of feedback. I gathered the problem stemmed from thermal shock. The V7 had a real thin section in it's casting and it cracked a lot.
    Well now I've been presented with a project to move a perfectly fine V7 to a garage so as to make room for a laundry room. I have an idea and was wondering if it's worth the trouble. Here it is.
    Would piping it P/S eliminate or at least mitigate the cracking problem? I think the HO is going to question the whole thing. A buffer tank or hydraulic separator would be a tough sell. Just looking for some affirmation.THX.
  • SWEI SWEI @ 2:06 PM
    Contact this user

    Minimizing thermal shock

    I'd be looking at a thermostatic boiler protection valve (ESBE, Caleffi, LK) to start with.  Outdoor reset control will also help.
  • Ron Jr. Ron Jr. @ 5:34 PM
    Contact this user

    Sounds like a budget project

    I'd suggest a simple bypass between the supply and return . The Burnham V8 manual shows how to pipe one in .

    I've also heard the problem with the V7s were sections near the cleanouts were cast too square and thin . And water flowing past there eroded the iron .
  •  