  • gcp13 gcp13 @ 4:35 PM
    Contact this user

    Too much to list

    Not sure what they were thinking
    I don't know where to start
    2 in header?
    Bullheaded tee,no swing joint
    16 in. A Dimension
    Level mains and back pitched drip returns
    Main air vents 27" above waterline, above boiler
    Plugged pigtail & 3/4 90 for presuretrol
    Hartford loop close nipple 2 " above waterline
    Auto feeder wired wrong not working
  • kevin kevin @ 7:40 PM
    Contact this user

    boiler

    Looks like that boiler should be in a pit.
  • JStar JStar @ 7:56 PM
    Contact this user

    Steam

    This is why drop-headers were invented. But, then again, knuckleheads think a dropped header is just a way to get a bruised toe.
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac
    http://facebook.com/thatcherhvac


    Guaranteed performance. Guaranteed energy savings.

    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    (Formerly "ecuacool")
  • kevin kevin @ 8:14 PM
    Contact this user

    drop header

    A drop header wouldnt work there, He said there is 16 in of a dimention. It needs to be in a pit or needs a condesate pump.
  • ChrisJ ChrisJ @ 10:41 PM
    Contact this user

    Header and pump

    In my opinion it needs a drop header and a condensate pump.
    Weil-McLain EG-45 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment

    Steam system pictures updated 6/5/14.
    https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#
  • Hap_Hazzard Hap_Hazzard @ 5:58 AM
    Contact this user

    Hartford Loop?

    It looks like a completely dry return to me. Probably not a good idea with that A dimension. It probably calls for water mid-cycle, so add "fluctuating water line" to the list of troubles.

    I'm not sure how you measured that A dimension. Is that from the max water line to the header? If there's more than 28" from the water line to the main a drop header should work.
    1983(?) Peerless G-561-W-S

    3" drop header, CG400-1090, VXT-24
  • gcp13 gcp13 @ 7:40 AM
    Contact this user

    A dimension

    I measured A dimension from where the
    Feeder satisfies the lwco.
    At that point it was 2 in below Hartford loop
    Close nipple
    It was a toss up weather to raise up above
    Close nipple or get as much distance as possible.
    I would like to pipe the drip down into a wet return and then back to the boiler
    Customer doesn't want to do any work yet ???
  • nicholas bonham-carter nicholas bonham-carter @ 9:25 AM
    Contact this user

    Bad install

    What were the symptoms which led to the service call?--NBC