The Wall
Forum / Oil Heating / steam oil to gas conversion
  • Post a Reply to this Thread
    steam oil to gas conversion (3 Posts)
  • Paul Paul @ 5:06 PM
    Contact this user
    how much will you save converting a modern oil steam boiler to a gas steam boiler approx. oil in mass is double the cost of gas. thx
  • Jamie Hall Jamie Hall @ 9:58 PM
    Contact this user
    If it's really a modern oil boiler
    the efficiency is pretty good already; you may have slightly better efficiency on gas, but your savings will come from the difference in the price of the fuel, not from replacing the boiler.  Which is considerable.
    Some boilers can be converted from oil fired to gas fired (not all); you might look into that first.
    Jamie
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • BobC BobC @ 10:09 AM
    Contact this user
    How is it sized?
    If the current steam setup is well matched to the heating load (EDR) the savings will be the difference in fuel costs, last year oil was running about $3.50 and NG in the Boston area was about $2.20 for the equivalent amount of gas (1.4 therms). We won't know what the cost is till the gas company posts this years winter rates that take effect at the end of October.
    If that steam boiler is oversized you can dial the output down to match the load by drilling the correct orifice size for the input BTU you need and that can save some fuel.
    Bob
    Smith G8-3 with EZ Gas @76,700 BTU, Single pipe steam
    3PSI gauge