The Wall
Forum / Strictly Steam / Pressuretrol set right?
  • Post a Reply to this Thread
    Pressuretrol set right? (6 Posts)
  • HelpMyHeat HelpMyHeat @ 5:01 PM
    Contact this user
    Is this pressuretrol (in picture) set right?
    It looks like it is set to 10 psi?
  • xcinek xcinek @ 6:52 PM
    Contact this user
    This is the 2nd pressuretrol
    This is the backup pressurestorl which means if the first one malfunctions
    this one will cut off the system and will not turn it on until you reset it with the red button.
    hope this helps
  • HelpMyHeat HelpMyHeat @ 10:43 AM
    Contact this user
    PSI
    Thank you.  Now, that I know that this is the 2nd Pressuretrol, does the PSI setting look right?
    It looks the setting is between 8 and 12 PSI.
    This seems rather high, no?  All of my radiator vents state to be careful about allowing any more than 10 PSI.
    Please advise.
    Thanks again!
  • Charlie from wmass Charlie from wmass @ 10:47 AM
    Contact this user
    You should find the setting on the other
    pressuretrol. the one that operates your system. This one is set at an acceptable setting as an Emergency back up. Do you have another one?
    cell # 413-841-6726
  • Rod Rod @ 10:52 AM
    Contact this user
    Backup Pressuretrol
    Hi- Assuming that you do have two pressuretrols, this is a back up for the pressuretrol that normally operates your boiler. Its job is to shut down the steam system before the safety valve opens at 15 PSI. This is just an addition saftety device and, with proper system maintenance, not ever likely to be activated. The pressuretrol that operates your boiler should be set so the maximum pressure is 2 PSI or less.
    - Rod
  • HelpMyHeat HelpMyHeat @ 9:34 AM
    Contact this user
    1st Pressuretrol found!
    Thanks for all your help! I found the 1st Pressuretrol on the side of the furnace and it is set to 1.5 PSI...
    Perfect!
    Thanks again!