The Wall
Forum / THE MAIN WALL / How to find a leak
  • Post a Reply to this Thread
    How to find a leak (9 Posts)
  • Garfield Garfield @ 9:17 PM
    Contact this user
    How to find a leak
    I have a triangle tube prestige 250000 btu condensing boiler that I installed about a year ago.  It has several webstone ball valves and 2 heat exchangers.  The boiler pressure is lower than the pressure on the other side of both exchangers. I have a small expansion tank  on the boiler loop.  I have a city line there with a regulator and a valve.  I keep it turned off in general.  About once a month the boiler shuts off on low pressure (about 8 psi i think)  then I turn on the valve and get it back up to about 15 and it's fine.  I understand this is adding calcium etc to the boiler loop and would like to find the leak but I don't know how.  The boiler loop is 1 1/2 inch sweat copper.  Thank you
  • RJ RJ @ 9:53 PM
    Contact this user
    leak
    Check the relief valve ,  some times hard to see if its leaking if its piped into another drain line
    RJ
  • Garfield Garfield @ 10:41 PM
    Contact this user
    evaporate
    It's piped to the floor and i don't notice any water there unless it's sporadic and evaporating before i notice it.
  • Zman Zman @ 8:38 AM
    Contact this user
    T&P valve
    It sounds like all the piping is in the boiler room and you have no puddles.
    I agree that the t&p or maybe the relief valve on the backflow preventer are suspect.
    I would watch the gauge as the boiler comes up from a cold start. If it rises, check the expansion tank. It is also possible the boiler has a leak. Does the condensate line drip when the boiler is not firing?
    Carl
  • Garfield Garfield @ 9:26 AM
    Contact this user
    Condensate
    Condensate does drip until the unit gets above 120 or so. How do I check the boiler for leaks?
  • Zman Zman @ 9:43 AM
    Contact this user
    Condensate
    It is supposed to drip when firing, Especially at lower temps.
    If you have a cold (off) boiler with a steady drip, that is a problem.
    Carl
  • RJ RJ @ 9:53 AM
    Contact this user
    dripping
    Is'nt the condensate from the flue gas
    RJ
  • Zman Zman @ 9:58 AM
    Contact this user
    Right
    In the somewhat unlikely event the boiler's heat exchanger has a leak, the water will end up in the condensate line. The normal condensate comes from the combustion.
    Carl
  • Garfield Garfield @ 10:58 AM
    Contact this user
    Caleffi backflow?
    The Caleffi series 573 backflow preventer is apparently leaking.  There is a small spot on the floor that's dry but the inside of the pipe is wet and there is oxidation around the end where the water apparently evaporates before hitting the floor.  It has always dripped a little when i opened the fill valve.