Forum / THE MAIN WALL / Hartford Loop?
  • Post a Reply to this Thread

    Hartford Loop? (10 Posts)

  • Mike Mike @ 3:57 PM
    Contact this user

    Hartford Loop?

    Despite the manufactures recommended piping inclusive of the traditional Hartford loop, is it acceptable to eliminate this when there is a boiler feed pump? Why?
  • Jamie Hall Jamie Hall @ 5:54 PM
    Contact this user

    One is inclined to wonder

    what happens if the check valve on the feed pump fails and there is no Hartford loop...

    but maybe I worry too much.
    Jamie

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • Mike Mike @ 4:35 PM
    Contact this user

    Hartford Loop?

    Hi Jamie,
    Thanks for the response. Of all the viewers, you appear to be the lone responder. We,ve communicated in the past. My answer to you would we to install a tee in the boiler feed tanks vent line. This way both LWCO's and the check valve would all have to fail before water would attempt to crawl out of the boiler.
    Mike
  • Jamie Hall Jamie Hall @ 8:17 PM
    Contact this user

    Sounds

    like it might well work..
    Jamie

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • JStar JStar @ 8:40 PM
    Contact this user

    Loop

    Feeding a pumped condensate return into a Hartford Loop can actually cause hammering and turbulence. You're better off sending it right into the boiler.
    - Joe Starosielec
    http://thatcherhvac
    http://facebook.com/thatcherhvac



    Guaranteed performance. Guaranteed energy savings.


    Serving all of NJ, NYC, Southern NY State, and eastern PA.

    Consultation anywhere.

    (Formerly "ecuacool")
  • Ron Jr. Ron Jr. @ 9:57 PM
    Contact this user

    Exactly !

    Those pumps shoot water back so fast that it travels up the equalizer and hits steam .  We install the HL anyway , as per manufacturer's specs  ..........  Can't risk the liability .
  • gennady gennady @ 9:22 PM
    Contact this user

    drip

    You will still need a drip for the header
    Gennady Tsakh

    Absolute Mechanical Co. Inc.
    www.AbsoluteMechanicalCoInc.com
  • Dan Holohan Dan Holohan @ 11:30 AM
    Contact this user

    I would

    Leave the header drip, which isn't an equalizer in this case, and I would pump into the bottom of that for the reason Ron mentions. That's the best way to keep returning condensate from bouncing up into the header and making the steam wet.

    If the receiver vent is higher than the boiler waterline it will serve as a sort of Hartford Loop should the check valve fail. 
    Site Administrator
    dan@heatinghelp.com













    Hug your kids.
  • vaporvac vaporvac @ 7:51 PM
    Contact this user

    That helps explain a nagging ?

    Thanks folks for that explanation. It helps explain why Slantfin doesn't recommend a HL when using a feed pump on their TR50s. Fortunately, they said I don't need that, but I have often wondered why it wasn't used.
  • jumper jumper @ 8:18 PM
    Contact this user

    matter of room

    In bigger buildings with bigger boiler rooms there can be an elevated condensate receiver so that there is no loop. Those situations call for condensate transfer pump instead of feed pump.
  •  