The Wall
Forum / THE MAIN WALL / does new boiler need combustion analysis?
  • Post a Reply to this Thread
    does new boiler need combustion analysis? (7 Posts)
  • Nom_Deplume Nom_Deplume @ 5:27 PM
    Contact this user
    Homeowner here. We're getting an HTP Elite FT.  I'm doing my homework in preparation for the install.
    The install manual (which i read online) says "If for any reason the throttle needs to be adjusted...use a combustion analyzer..." How strongly do I need to insist that the installers do a combustion analysis as a part of installation?
    I know from reading old posts that it is conventional wisdom to do a comb anal when installing, but don't modern boilers come properly adjusted? If not, why don't the install manuals tell installers to do it?
  • Aaron_in_Maine Aaron_in_Maine @ 5:38 PM
    Contact this user
    Yes
    Yes it needs to be checked. If your installer doesn't have an analyzer he shouldn't be installing it.
  • JStar JStar @ 8:23 PM
    Contact this user
    Combustion
    The manufacturer does require that the system be fine tuned with an analyzer. If you're not sure, call the manufacturer. Then ask what happens to their warranty if their directions aren't followed. If an installer doesn't have an analyzer and doesn't know exactly how to use it in order to fully understand how SAFE your boiler is, then what else are they not doing? What else is potentially unsafe?
    - Joe Starosielec
    732-494-4357
    j.star@thatcherhvac.com
    http://thatcherhvac
    http://facebook.com/thatcherhvac
    Guaranteed performance. Guaranteed energy savings.
    Serving all of NJ, NYC, Southern NY State, and eastern PA.
    Consultation anywhere.
    (Formerly "ecuacool")
  • Jamie Hall Jamie Hall @ 9:01 PM
    Contact this user
    They absolutely
    need to be fine tuned after installation.  Yes, they will be close right out of the box -- close enough so they will start and run.  But every installation is slightly different, and you have to adjust them for best reliable performance -- and the only way to do that is with a combustion analyser, properly used.  No excuses.
    Jamie
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • Ironman Ironman @ 9:21 PM
    Contact this user
    Analyzer is an absolute necessity
    Jamie,
    As usual, we're in agreement. Anyone who doesn't have an analyzer and who is not trained to use it, has no business installing a mod/con.
    I will have to disagree about it running right out of the box, though. I've had more than one that were so far out of adjustment that they would not fire out of the box.
    Bob Boan
  • Yorkietom Yorkietom @ 5:38 PM
    Contact this user
    testing
    As I was taught years ago, if you're  not testing you're guessing ! Definately test and most states its code.
    Tom
  • Nom_Deplume Nom_Deplume @ 9:53 PM
    Contact this user
    thanks!
    Thanks for the advice! Boiler was combustion tested and was good out of the box (I have a report with the readings).