  • nicholas bonham-carter nicholas bonham-carter @ 7:00 PM
    Contact this user

    Small stone church

    2200 sq ft, with infrequent use. Well shaded, so how much cooling would I need if there are 90 people inside, and the ambient air temp is 90 degrees.--NBC
  • Ironman Ironman @ 12:37 PM
    Contact this user

    Latent Load

    Figure 230 btu's latent load per person. Then match it to the latent capacity of the equipment you're considering.

    The latent load from body heat will almost always be larger than sensible heat from bodies or structure in any meeting house when compared to the capacity of the equipment.

    The latent capacity of most modern equipment is about 25-28% of the total. So, 90 x 230 = 20700 / .25 = 82,800 / 12,000 = 6.9 tons. Call it 7 tons or 7.5 if you use a package unit. Keep in mind, this doesn't include any make up air which most codes will require. Usually 5 - 15 cfm per person. 90 x 5 = 450cfm. That's at least another ton if the 5cfm requirement is used.
    Bob Boan



    You can choose to do what you want, but you cannot choose the consequences.
  • nicholas bonham-carter nicholas bonham-carter @ 8:39 PM
    Contact this user

    thank you very much

    when you see these pictures of the chapel, you will see why we cannot use an ordinary approach to heating and cooling.
    http://www.forestlawnomaha.com/images/chapelpics2.htm
    I want to investigate using a boiler and chiller with some [hopefully] innocuous looking cabinet fan coils. if I can raise enough money, maybe we could use geothermal, and not have a noisy condensing unit outside!--NBC
  •  