  • WeatherizationNYC WeatherizationNYC @ 12:03 PM
    Contact this user

    Turbomax Storage - LIFO or Symmteric?

    Good morning,
     
    I’m looking at two Turbomax storage tanks which were to be piped in Last-In-First-Out order, according to spec.  The contractor piped them symmetrically instead. 
     
    Can anyone tell me whether the symmetric piping arrangement will cause any problems, impact the lifetime, etc?  Should I have him re-pipe it?

    Thanks in advance.
  • Zman Zman @ 12:07 AM
    Contact this user

    Not a problem

    I think a simple symmetric header will work just fine. The objective is even flow. Both piping strategies will accomplish that.
    Carl 
  •  