    tekmar 256 (7 Posts)

  • Paul S Paul S @ 1:46 PM
    Contact this user

    tekmar 256

    I was called on a job to wire a boiler using a tekmar 256....a different heating contractor installed boiler and could not wire customer provided control...I know how to wire it but when you have to put in what type of radiation is being used what do I put in if there's a combination of baseboard and radiant heating.....?....there is no boiler protection loop for low return water temp...thanks Paul S
  • SWEI SWEI @ 2:07 PM
    Contact this user

    Tekmar curves

    From http://tekmarcontrols.com/images/_literature/e0003_06.pdf

    There is a minimum target temperature setting for the boiler that sets the bottom of the curve.
  • Zman Zman @ 11:28 PM
    Contact this user

    256

    Paul,
    The 256 will control the boiler with outdoor reset. You can set the boiler minimum output.
    It is not designed for two temp systems or boiler protection.
    Carl
  • Paul S Paul S @ 6:55 AM
    Contact this user

    256

    I can still use it right?....do they make a control for 2 temp systems? Thanks paul S (in other words what type of control you wouldve used on a application like this)
    This post was edited by an admin on November 11, 2013 6:57 AM.
  • SWEI SWEI @ 10:43 AM
    Contact this user

    Two temps

    A 363 will manage two separate reset curves.  They're somewhat pricey.

    I'd probably just add a Taco iSeries-R for the RFH.
    This post was edited by an admin on November 11, 2013 10:45 AM.
  • Paul S Paul S @ 6:47 AM
    Contact this user

    tekmar 256

    How come this control has a room occupied temp setting and a unnoccupied temp setting if it does not actually sense temp....i believe its a parallel heating curve ...can someone explain that? thanks paul s
  • SWEI SWEI @ 5:27 PM
    Contact this user

    It's a curve shift

    triggered by an external signal.
  •  