    NEW STEAM BOILER IS BANGING! HELP!

    I had my steam boiler replaced less than a month ago. The day after it was replaced, the pipes started banging every time the boiler kicked on. The plumber came back and put a treatment in to skim the oil out of the pipes better. A day later the banging started again. He has been back to skim it 4 or 5 times and each time we can go about 2 days until the banging starts up again. The banging is in the pipes and is LOUD. Once it starts banging, the heat simultaneously stops traveling to one side of the house.

    Can anyone give any suggestions to help me figure out this problem???
  • STEVEusaPA STEVEusaPA @ 8:51 PM
    Contact this user

    For starters,

    You may wish to repost in the steam section with some pics of the near boiler piping. The fact that a 'plumber' skimmed it '4 or 5 times' tells me he doesn't know what he's doing. It's most likely piped wrong, water line was changed, or some other changes were made that the installer didn't think mattered, but obviously do.
    What type of boiler?
    Could also be something as simple as allowing main pipes to now sag. Or insulation missing, etc.
    steve
    This post was edited by an admin on December 1, 2013 8:53 PM.
  • It Sounds Like

    The near boiler piping is wrong, it's a common problem with a new Steam Install.
  • nicholas bonham-carter nicholas bonham-carter @ 8:59 PM
    Contact this user

    New hammering boiler

    Post some pictures here of the boiler and it's piping.
    What pressure is the boiler running at?
    More skimming will be required, and you should be able to do that, (do a search here for details). You will also want to flush out any chemical which he may have put in the boiler, before it becomes welded to the bottom. The only chemical in the boiler should be H2O, unless you have a Chloride problem in your area..--NBC
  • broken_furnace broken_furnace @ 9:05 PM
    Contact this user

    pictures

    This is the newly installed boiler and photo of one of my radiators. I am told its a two pipe system. Old boiler only had one pipe coming out of the top and piping was different on side.
  • Weezbo Weezbo @ 9:41 PM
    Contact this user

    That looks pretty tidy .

    it has nice grade steam looks like it would be clean ,
    do you have time for one more pic to the left of the pic we are looking at and one that goes over to the right closer to the pipes where there is some copper ?

    Thank you .
    Weezbo .
    This post was edited by an admin on December 1, 2013 9:48 PM.
  • TonyS TonyS @ 1:52 PM
    Contact this user

    no swing joints

    on the top of the risers. Not that this is your problem but unlikely to be covered by boiler warranty if boiler snaps.
  • nicholas bonham-carter nicholas bonham-carter @ 9:18 PM
    Contact this user

    Noisy new boiler

    I don't see any errors in the piping, so perhaps skimming will cure it and very low pressure, as this is a trapless system, which may need orifices to restrict the steam to just that amount the radiator can handle. I can't think of the name for it or you could be reading about it in the library here.
    Get him to replace the pipe from pressure relief valve to the floor, so as to prevent any accidents.--NBC

    http://www.heatinghelp.com/forum-thread/84821/Mouat-Vapor-Heat-Steam-Traps
    This post was edited by an admin on December 1, 2013 9:21 PM.
  • N/A @ 9:40 PM

    why that brand??

    As far the pixs shown.. no amount of skimming will cure it thru the tiny 3/4 skimming port.. should be full sized nipple for proper skimming. 2nd, with trapless radiators, are the return legs trapped below, pressure must be very low,low ,so low u can't see the needle move on gage... lastly, why is the relief valve pipe disconnected?? Someone added chemical to boiler?
  • it looks like

    You should have two tees coming off the steam header to feed both steam mains evenly.
  •  