  • MikeyG MikeyG @ 11:58 AM
    Contact this user

    Thermostatic Rad Valve Control

    Hi-
    I am a homeowner and not a professional.  I purchased the following products and installed them (after reading Dan's books) for one room where I have a second heating source to shut down the steam rad if the room reaches a certain temperature:
    Thermostatic Rad Valve w/ Vac Breaker for one pipe steam -- Danfoss SKU:013G0140 Remote Setpoint & Sensor - Wall Mount -- Danfoss SKU:013G8562 
    from Pex Supply
    However, it does not seem to be working as the rad gets hot immediately regardless of the temp in the room (even if I adjust the thermostat of the remote sensor to the lowest setting.)

    Can anyone suggest whatn the problem may be?  Thanks in advance.
    Mike G.
  • MDNLansing MDNLansing @ 12:33 PM
    Contact this user

    High and Low

    EDIT

    Removed as this is not the electric control I was referencing.
    This post was edited by an admin on December 4, 2013 2:45 PM.
  • JeffM JeffM @ 2:01 PM
    Contact this user

    non-electric

    That looks to me as if the actuator is a non-electric (capillary) model, so it uses a tube and fluid pressure to control the actuator, not electricity. A multimeter won't help in that case.
    In many cases if a capillary control is not working properly the capillary tube has been pinched or kinked at some point. With a kink, pinch, or hole in it the fluid can't transmit pressure from the dial to the actuator and it won't work. These capillaries aren't too delicate, but need to be handled with some care or they can be damaged (don't drop anything on them, put tight staples over them, or pull them tight around corners).
  • RJ RJ @ 4:43 PM
    Contact this user

    Danfoss

    the boiler/steam system must go to 0 psig on off cycle and have a numerous cycle rate for these 1 pipe valves to work correctly, if the system never draws air in the Danfoss valves often wont close.   I posted the details in the past and believe I sent a document from Danfoss (1983) to the archives
    RJ
  • MikeyG MikeyG @ 6:27 PM
    Contact this user

    Cannot locate the details you posted in the past ...

    Hi RJ. 
    I've tried to search for what you posted in the past and perhaps I just am not that good with searching this site but cannot find anything.  Would it be possible to help direct me there?  Thanks!
    Mike
  • MDNLansing MDNLansing @ 8:35 PM
    Contact this user
  • RJ RJ @ 4:53 PM
    Contact this user

    r_stahmer@yahoo.com

    type Danfoss in the site search   look for July 29 2009  old document from Bill Burton