    Puzzler: Condensate Return Leak, LWCO, Auto Feeder

    Looking for some thoughts from the wise people
    here.  We have determined that there is probably a leak in our buried
    condensate return piping, and I'm trying to sort out if our float-type
    LWCO may also be malfunctioning.

    My system: HB Smith 2500L
    steam boiler with domestic hot water coil.  Runs on a Heat-timer
    EPU-CH.  McDonnell & Miller 67 float LWCO with McDonnell &
    Miller 101-A water feeder.  McDonnell & Miller probe LWCO with
    automatic reset, just below the bottom level of the sight glass. 
    Hartford loop an inch or two below the probe LWCO (seems a bit lower
    than usual).

    Symptoms: Waking in the morning with no heat
    or hot water.  This only happens when night temperature does not call
    for heat and the system is idle through the night.  I check the boiler
    and there is no water visible in the sight glass, the red light is
    blinking on the probe LWCO.  I fill the boiler manually by pushing the
    button on the water feeder and as soon as the level reaches the probe,
    the burner fires up.  This takes about 2 or 3 minutes, and after another
    2 or 3 minutes the water level is nearly at the "normal" line.  After
    this the system runs normally as long as the Heat-timer calls for heat
    and cycles steam once per hour.  I have put the Heat-timer in summer
    mode and observed that the water level dropped about 2" over a 2 hour
    period.

    Hypothesis #1: Water is slowly leaking from the
    system and the float LWCO is sticking and not signaling the water feeder
    to work.  Water continues to drain and the probe LWCO eventually shuts
    the system down.  I like this hypothesis because the system seemed to
    produce hot water fine for the summer and our leak is only now being
    exposed because the LWCO is malfunctioning and not turning on the water
    feeder.  The only reason I am in doubt is that everything still runs ok
    as long as there is a call for heat.  We know there is a leak, so at
    some point the float LWCO must be triggering the water feeder.  Is it
    possible that the flow of water through the return piping during steam
    production slows the leak enough to not require makeup water?  Or maybe
    just the way water is moving through the system prevents the float from
    sticking?  Also note: when the system is producing heat, opening the
    blowdown valve on the float LWCO does actually trigger the water feeder.

    Hypothesis
    #2: At some point during the night, water leaks quickly from the
    system.  The float LWCO signals the water feeder to turn on, but it
    cannot keep up, and eventually the float LWCO turns everything off,
    including the water feeder.  Water level continues to drop until the
    probe LWCO also activates (Do these LWCOs turn off the water feeder if
    the cutoff water level is reached?).  I have doubts about this
    hypothesis as well because I would think that the float LWCO would need
    to be reset by bringing the water level back to near normal before the
    system would turn on again.  As I said before, the system turns back on
    as soon as water reaches the probe LWCO, which is well below the float
    LWCO.

    Thank you all for reading and I hope you can help me solve this puzzler.
  • ALIGA ALIGA @ 9:52 AM
    Contact this user

    I would start by fixing the leak

    And then You can monitor the feeder
  • sreja sreja @ 10:40 AM
    Contact this user

    re: uzzler: Condensate Return Leak, LWCO, Auto Feeder

    I'm just an amateur so take my thoughts with a grain of thought.

    I too would guess that the problem is the main LWCO/feeder switch getting stuck and unstuck -- we recently had that happen to us.  (ps. A quick fix to that stuck float valve was a hard punch to the LWCO).

    We also have a buried return leak that is impractical to fix, which indirectly causes more fresh water and thus rust in the water.

    I would suggest a first step of installing a new water feeder that measures the amount of fresh water fed into the system.  There is a VXT model that it mentioned on the forum a lot that works fairly well.

    That's what we installed and it is absolutely essential to understanding the nature of the water loss.  It will let you see how much water you are losing and when.

    With that information you can both diagnose how bad your leak is, and when the LWCO is calling for water.

    As soon as you conclude that it's unlikely that your system is simply calling for so much water that its purposefully shutting down the boiler, and you conclude that the LWCO float is getting stuck in some fashion, i would replace (or clean?) that LWCO float switch.  I get nervous about relying on the backup LWCO so yeah, if in doubt i'd probably replace the LWCO float/feeder sooner rather than later.
  • nicholas bonham-carter nicholas bonham-carter @ 9:40 AM
    Contact this user

    Greetings from long ago and not so far away

    Has that lobby return leak got worse, or is it difficult to tell?
    Maybe it should be on your New Years resolution to do some repiping!
    Let's start a new thread on that.--NBC
  • Jamie Hall Jamie Hall @ 11:13 AM
    Contact this user

    Seems to me

    that something is slightly amiss with the controls (as well as the leak, patience).  In my view, either low water cut off should shut off the system, and it shouldn't run at all until both are happy.  The behaviour you describe, where it will turn on when the probe type unit is satisfied, even though the float unit isn't, and the water feeder doesn't activate automatically under those conditions, suggests very strongly that the float unit isn't working properly.

    It is possible that the vibration of the boiler firing may be enough to allow the float unit to operate properly and activate the feeder, and that the leak is enough so that at night when the boiler isn't firing the water level drops below both LWCOs (the float unit having hung up) and shuts the system down.

    They can be cleaned (you do flush it once a week or two, don't you?) but once they start hanging up it is -- in my humble opinion -- better to replace them.  This is a safety device, after all...

    Now that leak.  2 inches in 2 hours is wildly excessive.  Even if you get things fixed so that the boiler will run, that much fresh water is going to corrode that boiler and give you more, and more expensive, problems.  Find it and fix it.
    Jamie

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • zwiegand zwiegand @ 12:01 PM
    Contact this user

    Replace LWCO, Install Meter

    Thanks to those who have commented so far.  The consensus seems to
    be that the float LWCO is malfunctioning.  We are definitely planning to
    find and fix our leak, but it will take time because our return pipes
    are buried in the basement of a commercial space that we do not own. 
    Anyway, I think our immediate plan should be to replace the float LWCO
    and to install a meter on the feed line.  Any thoughts on whether the
    meter should be upstream or downstream of the feeder?  In our case it
    would be much, much simpler to install it on the output side.

    Thanks again for the help everyone!
    This post was edited by an admin on December 7, 2013 12:32 PM.
  • Rrey Rrey @ 8:39 AM
    Contact this user

    Test to be sure

    Test the return.
    Any time I suspect a return leak, i perform the following test:
    Cut the return loose on each side of the point were it disappears into the floor (Yes, I know, it's a pain bc it's iron piping, so you may have to need to add a cpl of unions and replace back to the next fitting, if you don't have a threader)
    Try to do it at roughly the same height on each side.
    Fill the return with water and monitor it for bit and see if the water level goes down.
    This will confirm a leak beyond any doubt.
  • sreja sreja @ 10:33 AM
    Contact this user

    re: test

    Thanks for that testing advice -- that's actually a pretty good idea that could come in handy..
  • RJ RJ @ 10:50 AM
    Contact this user

    lwco

    lwco can be taken apart and cleaned, the sa101 has a strainer that should be cleaned or replaced at least every 6 months, a plugged up lwco could be part of the problem as others have said 
    RJ
  •  