The Wall
Forum / THE MAIN WALL / Oversized boiler
  • Post a Reply to this Thread
    Oversized boiler (3 Posts)
  • TonyS TonyS @ 11:11 AM
    Contact this user
    Oversized boiler
    I went to look at a job that was put in a few years ago, its got everything, cast rads in the old section, baseboard fin and radiant in the new. Complete disaster!
    The boiler was installed a few years ago also, Burnham cast iron 170k ,its about a 100k over sized. Question is ...How do you guys feel about removing burners to down fire this beast. PROS...CONS AND TECHNIQUES ?
  • Ironman Ironman @ 11:23 AM
    Contact this user
    I Wouldn't Do It
    Tony,
    I wouldn't do it under any circumstance. If you do, you own it and all the ramifications that come with it. It's illegal to modify the gas train in a manner not approved by the manufacturer and AGA. I'm sure Tim can give better specifics.
    I'd look at a buffer tank or a properly sized boiler.
    Bob Boan
  • Tim McElwain Tim McElwain @ 3:31 PM
    Contact this user
    Not a good idea for a couple of reasons
    1. The overall efficiency will be affected as you still have to heat all the sections
    2. Safe ignition can also be a problem depending on what burners are blocked off.
    3. It could affect the warranty on the boiler if that is still a factor depending on age
    4. Manufacturers of equipment will not authorize such a move.
    You can by changing all the orifices to smaller size or adjusting pressure typically reduce input about 10% which is not the best but better than blocking off burners.