Forum / Radiant Heating / Thinking of replacing existing pump for a Taco Bumble bee pump
  • Post a Reply to this Thread

    Thinking of replacing existing pump for a Taco Bumble bee pump (10 Posts)

  • Total1 Total1 @ 5:26 PM
    Contact this user

    Thinking of replacing existing pump for a Taco Bumble bee pump

    Thinking of replacing existing pump for a Taco Bumble bee pump .


    https://www.taco-hvac.com/en/products/products.html?current_category=405


    On my Vitodens 100 system .

    Ideas ?
  • Harvey Ramer Harvey Ramer @ 8:10 PM
    Contact this user

    Why?

    Why?
  • delta T delta T @ 9:14 PM
    Contact this user

    Looks like a...

    WIlo you have installed. Very good pump, pretty much all I use. I second the question...Why? do you have any problems with system?
  • Total1 Total1 @ 10:35 PM
    Contact this user

    Like the idea of the pump

    Like the idea of the pump adjusting to the boiler temperature and keeping the delta T the same .  No problems at all with the system , but the new pump would use 85 % less power and has a cool look factor .. 
  • Tom Tom @ 6:18 AM
    Contact this user

    and noisy

    The bumble bee is much louder than normal pumps. If thats a factor.
  • Chris Chris @ 7:36 AM
    Contact this user

    WOW

    LWCO is in the wrong place though it doesn't matter because the boiler won't fire anyway if you don't make the flow switch..With the boiler needing a min flow rate of 1.7gpm across the HX and you are not piped pri/sec wouldn't recommend it unless your going to run it in a constant pressure mode.

    What's with that zone valve and the ball valve? Some sort of by-pass?
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."
    This post was edited by an admin on January 31, 2014 7:37 AM.
  • Total1 Total1 @ 8:44 AM
    Contact this user

    hmm

    Why is the LWCO in the wrong place ? It is the highest in the loop  , where would you put it ?  .  The zone valve / bypass is for the room / tunnel under the garage to get enough flow to start the boiler . 
  • Chris Chris @ 9:27 AM
    Contact this user

    huh?

    That's why the boiler should have been properly piped primary secondary. Sure hope you never need more then 6.2gpm...LWCO is useless so it doesn't matter...
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."
  • NYplumber NYplumber @ 10:36 AM
    Contact this user

    Dont mess

    Dont mess with a high head hx and dt. If you slow the flow too much you will loose more then you gain.
    :NYplumber:
  • Total1 Total1 @ 4:43 PM
    Contact this user

    ok

    With this on demand boiler , since it keeps no water warm when it shuts off , and the pump is controlled by the boiler also  , I have no need to circulate the water when it is off . The Gas inspector wanted a LWCO installed , I even quizzed him on why one is needed with the flow switch . This boiler is ONLY heating my garage , room / tunnel below the garage , and later project floor heat for the bathroom in the basement , all is good and thanks for your input . I will keep it how it is . To keep around 1100 sq ft of floor heated it averaged out to be 1 $ per day @ 60 F , even when it was -36 C .
  •  