  • Jrg23 Jrg23 @ 6:46 PM
    Contact this user

    Air in system

    Okay i have tried everthing to get air out of two zones in a hotel. Each room comes off of a monoflo loop with a zone valve on the supply side. i bleed the air out of return side hosecock and room is fine for the day the following day its back. I have looked for leaks in system and all looks good. so not sure what else to do very frustrating.

    Any thoughts would be great.
  • kcopp kcopp @ 7:16 PM
    Contact this user

    Is it air locking ....

    up or just gurgling? I would add a 1/2cup of dawn/ Ajax dishwashing soap.. Raise the system pressure to 18.  pretty sure it will work. Let us know.
  • M Lane M Lane @ 10:15 PM
    Contact this user

    Air Vents

    Any out remote along the piping run? Like at a high point? Maintenance guys add them all the time thinking that'll solve problems. An auto vent say at a baseboard or in the attic will actually suck air in.
    This post was edited by an admin on February 1, 2014 12:42 PM.
  • N/A @ 10:17 PM

    new boiler?

    New boiler with new pumps piped incorrectly?? Got any pictures??
  •  