    Hard Grey buildup in radiant system (5 Posts)

  • NRT_Rob NRT_Rob @ 5:39 PM
    Contact this user

    Hard Grey buildup in radiant system

    I have a client who is getting a hard grey buildup in his radiant system, making valves stick etc. it's o2 barrier pipe, geo system with a buffer tank, fully closed and when they close the makeup valve there is no pressure drop, so no leak.

    I'm kind of astounded at how much buildup can occur apparently from the single fill of water... admittedly, it's probably about 200 gallons of water, but still.

    buildup is hard enough to require chiseling with a screwdriver to remove.

    anyone else ever seen such a thing? client will send out a water sample for testing but would love to hear if anyone's seen it before.
    NRT.Rob
  • Harvey Ramer Harvey Ramer @ 5:55 PM
    Contact this user

    Dissimilar Metals

    More than likely caused by dissimilar metals. Water being the catalyst that connects them. You will probably need to use an inhibitor to stop the process.

    I know a girl who has a long metal pin in here Femur. As a result she can't were any jewery. It just turns green from corrosion. In that case, her body is the catalyst that connects the dissimilar metals.

    My thoughts.

    Harvey
    This post was edited by an admin on February 28, 2014 5:55 PM.
  • Weezbo Weezbo @ 6:49 PM
    Contact this user

    on one or two places,

    over the years i noticed something like that.
    my thought at the time is
    'This looks a Lot like gypcrete or cement or maybe Blue clay. '

    thing is, it was under pressure ,
    and,
    tested prior to the pour ,
    in both cases and did not have any way for it to get into the system .
    so i am going to go with Harvey on this.. is there perhaps a piece of galvy anywhere including the potable water ?


    i know ....take a look in the strainer of the fast fill maybe this is being introduced thru that system ....
    This post was edited by an admin on February 28, 2014 6:53 PM.
  • SWEI SWEI @ 7:34 PM
    Contact this user

    Lab analysis

    of both feed water and exsting system water would be in order.
  • Mark Eatherton Mark Eatherton @ 11:19 AM
    Contact this user

    Any magnesium or aluminum anodes?

    If they were in contact with the system water, could be they are plating out?

    I've never seen it myself.

    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  •  