    Sizing steam boiler with indirect water heater (2 Posts)

  • Ed59 Ed59 @ 9:48 PM
    Contact this user

    Sizing steam boiler with indirect water heater

    Hi, I know my new steam boiler needs to be sized to the EDR of the radiators, plus piping pickup, but does it need to be increased for an indirect water heater?

    There's a chart on page 8 here, http://www.htproducts.com/literature/lp-83.pdf
    but it's unclear to me. I'm not even sure what the units in the chart are or what they're applied to. And there's a note ": IT IS NOT RECOMMENDED TO REDUCE BOILER INPUT WHEN USING DOUBLE WALL TANKS." Meaning the boiler size DOESN'T need to be reduced for those??
  • Charlie from wmass Charlie from wmass @ 10:00 PM
    Contact this user

    usually it does not

    need up sized for domestic. As long as it is sized for the EDR and there is not a crazy amunt of hot water needed.