The Wall
Forum / Controls / Multiple Circulator & Zone Valve Relays with Post-Purge?
  • Post a Reply to this Thread
    Multiple Circulator & Zone Valve Relays with Post-Purge? (3 Posts)
  • Steamhead Steamhead @ 5:06 PM
    Contact this user
    Looked at a HW job yesterday with six circs and four zone valves. The control system for this looks like someone threw a whole bunch of spaghetti onto the wall and it stuck. Since we'll probably be re-wiring this, does anyone know of a mutiple circulator or zone valve relay that will allow the circs to purge some of the heat out into the zones after shutting off the burner?
    TIA.
  • hot rod hot rod @ 10:52 PM
    Contact this user
    does it have an indirect?
    if not the priority relay output on most pump relays has a post purge. I know the Caleffi ZSR has a non-adjustable 2 minute post purge on relay 1
  • STEVEusaPA STEVEusaPA @ 1:32 PM
    Contact this user
    Make your own
    Unless someone has some commercial controls experience, you may be better off getting your own relays/contactors (Grainger's) and making it yourself.  I know a real wizard up here in the Philly Suburbs who used to build/service elevators before he started his HVAC career. I've seen him do some interesting things with relays and contactors.  Send me a message if you want his info.
    Tekmar boiler controls (I know the 374 does) also post purge on the DHW contacts ( think until 10 or 20 degree drop).
    steve