    Electro Zone valve control issues

    I am in a bit of a bind. I am working on a 3 zone system that has 20 Volt DC, NOT AC, valve controls.  They are called Electro Zone and apparently went out of business in the early 70s. I cant find any info on them and hoping someone here may be able to lend some assistance.
    Three coils and they all OHM fine. Coil issue can be ruled out. With one zone on, I read 19.4 volts, with two or three on, I read 18.1 volts. I wonder if this is enough to open the valves or not.  I am really not sure where to go from here or how to troubleshoot these valves. Any advice is appreciated.  Thanks.
  • icesailor icesailor @ 2:27 PM
    Contact this user

    DC Zone Valve coils:

    Are you sure that the coils are DC? Does it have a rectifier to convert the AC to DC?
    Are they wax motor expansion valves or are they rotor motors that rotate a valve open?

    Can you take photos of the valves? Do you know what an "Amp Mate" is that measures the amperage through the valve from the thermostat, through the valve and through the coils?
  • icesailor icesailor @ 2:33 PM
    Contact this user

    Electrozone valves:

    There was a discussion here in 2005 about them.
    Here is another one in 2011 about them.
    It seems that the best thing to do is replace them. It shouldn't be a biggy. The newer Taco zone valves work well. I always used wax motor 572's but I was happy with the last ESP Taco valves.

    https://groups.google.com/forum/#!topic/alt.home.repair/lQLcSJgxRGQ