N/A February 27, 2003 @ 11:25 PM
Thank you Slant/Fin
once again a quick response and great techncial assitance from Jim Sokolovic the guy in the Lab who is always a big help. Thanks for the response Steve. Will call tomorrow and get the change out for this obsolete and defective Integrated control. -
N/A February 26, 2003 @ 8:40 PM
Prodigy 21 Model KC-100
with a RAM Model H1MC5-01 Integrated Control Board. Does anyone have specific information on this board and its operation. Followed the exact procedure for setting up system as outlined in Slant/Fin instructions everything checks out. Getting intermittent operation on the board. I want a procedure for checking the electronics on the board. I have these for Honeywell and United Technology boards but not this board. I am getting two different microamp readings depending on direct from flame sensor or from flame current jack. I am reading 15 microamps at jack, 5 microamps at sensor??? No one locally has this board. -
Slant/Fin Prodigy boiler
Timmie, Our head technician on that product will contact you by email this morning. He understands the operation of the control better than any one else. Steve