The Wall
Forum / THE MAIN WALL / CO levels from oil burner
  • Post a Reply to this Thread
    CO levels from oil burner (47 Posts)
  • John McArthur John McArthur @ 1:35 PM
    Contact this user
    CO levels from oil burners
    I just got a new testo 330-1. i was using a dwyer wet type analyzer.I have a customer with an oil fired boiler.this burner is making about 300ppm of CO with abt 11percent CO2 whats normal? Ive never had a tool that I could read this with.I just know the other burners Ive had the testo on are running CO in the single digits.Am I seeing flame impingment? thanks mike
  • Dave Yates (PAH) Dave Yates (PAH) @ 2:34 PM
    Contact this user
    missing
    What's the O2 reading? Sounds like you're on the fuel-rich side of the CO2 scale. To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jim sokolovic jim sokolovic @ 2:43 PM
    Contact this user
    11% CO2 = 6% Oxygen...
    for oil - that's slightly lean or diluted for most applications?
  • Dave Yates (PAH) Dave Yates (PAH) @ 3:25 PM
    Contact this user
    CO2 reading
    can be identical on either side of the scale: fuel or O2 rich Fuel-rich side will see much higher CO readings Here's a link to why: http://www.bacharach-training.com/combustionzone/advantages1.htm To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jim sokolovic jim sokolovic @ 8:49 AM
    Contact this user
    Quite a while back there was a discussion on this here...
    but I would believe that certain characteristics of the flame would clue you in that you are not on the right side (lean fuel) of the air/fuel relationship. I would think that being rich on fuel past the stocio point would produce a tremendously hazy flame with heavy smoke with oil that would be hard to not notice?
  • Dave Yates (PAH) Dave Yates (PAH) @ 9:50 AM
    Contact this user
    sometimes, but not always
    I've seen units that supposedly had been tuned and cleaned for seasonal service that were on the fuel-rich side and smoke testing delivered a #6 or higher. Flame "looked" ok. A recent one I inspected had run great for 14 years until an inexperienced tech adjusted the flame - by eye. Less than a month later,it was clogged shut with soot. No O2 test or smoke test had been performed. The job ticket listed CO2 and a net stack temp that equaled 81% efficiency. The only problem? That unit isn't capable of achieving 81% and the manufacturer's literature specifies the best you can get is 75%. The real net stack temp (which was much higher) when combined with the actual CO2 equaled exactly 75% once the air was adjusted to a trace smoke. O2 was 7.5%, which also was within the range specified in that manufacturer's 1990 literature. BTW, the correct nozzle was in place acording to the annual service sheets. All of the components (CO2; O2; net stack; draft over fire & in breech; smoke)are necessary for a complete picture. If you're not testing for O2, you're taking one heck of a chance for producing large quantities of CO. A combustion analysis done prior to the annual clean & tune, followed with one done afterwards works wonders for convincing owners to have that annual check. My old "dumbbell" combustion analyzer sets served me well, but the newer electronic analyzers we now use are almost too easy and the printout is a great CYA (cover your assets) plus the HO likes to get a copy instead of just a verbal OK. To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jim sokolovic jim sokolovic @ 10:46 AM
    Contact this user
    So does the Oxygen reading...
    stay at zero when you are fuel rich beyond this point? Or does it start climbing once past it, as the CO2 starts to drop again. Most combustion analyzers calculate CO2 from the Oxygen reading (if they only have an Oxygen sensor). Isn't the relationship always maintained? If a tech isn't using a smoke gun at least, I don't know what to say about their practices!
  • Dave Yates (PAH) Dave Yates (PAH) @ 11:08 AM
    Contact this user
    news to me
    Jim, That's news to me that the CO2 is derived from an O2 sensor, but I don't make the equipment & can't answer that question. Man, I hope that's not the case. Looking at the charts indicates the O2 should read zero at best if on the fuel-rich side, yet the S-chart indicates CO2 can be mirrored on either side of the chart. Next time out, I'll have to adjust the air band into the fuel-rich zone and test our equipment to see if we get any O2 readings with a mirrored CO2 percentage. It'll be interesting to see how high the CO percentage goes as smoke gets worse. I'll want a second test instrument measuring CO in the room while fooling with the fuel-rich side. To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Firedragon Firedragon @ 11:05 AM
    Contact this user
    Jim,
    I went over all of my stuff and came up in the same place, so I went searching for a layman's view to simplify it for all of us. No luck and that was even going through the member's archives of the Combustion Institute, go figure! Then I tried another approcah and found this: http://www.planet-equipment.com/index.html?gasanalysis.html
  • jim sokolovic jim sokolovic @ 11:39 AM
    Contact this user
    Grrrrrrrrrrrrroooooooooooooooaaaaaaaaaaaaan!!!!!!!!!!!!!!!!!
    O.K. - Went there and read the "Exhaust Gas Analysis" section. Here are some excerpts: "From this point on (past stociometric), even if we keep enrichening the mixture, O2 will read zero" "Here's a little secret. O2 and CO should generally be about equal. Tell your friends about this" "CO2 is inversely proportional to O2. In other words, if one goes up, the other goes down" Obviously, none of these statements supports the others. The second one is a real doozy - so, at zero% O2, we should expect zero% CO? This site is for analysers of automobile emmisions anyway, so maybe the same rules don't apply - I still find it contradictive and dangerously misleading!
  • Firedragon Firedragon @ 1:13 PM
    Contact this user
    Sorry Jim, I keep trying and hydrocarbons
    are hydrocarbons and believe it or not it actually mirrors Bacharach's stuff, JMO!
  • jim sokolovic jim sokolovic @ 1:23 PM
    Contact this user
    George, you are one of the many...
    people here that totally amaze me with your knowledge, dedication, and willingness to share. I guess I'm just stuck on something that doesn't make sense to me, and since I'm mostly familiar with combustion stuff... well, you know how it is. But don't you also see the dilemma, here? Thanks for trying, though - no need for apologies!
  • Firedragon Firedragon @ 1:32 PM
    Contact this user
    Tell you what,
    send me an e-mail and I'll put you in touch with my 'expert'.
  • jim sokolovic jim sokolovic @ 3:26 PM
    Contact this user
    Than you, George - I spoke to...
    Bill at Testo. He was able to answer the following without any reservation: 1- Oxygen reaches zero at stociometric and will stay at zero at all fuel rich points beyond that, providing the combustion can be maintained. 2- A combustion analyzer that calculates CO2 from the Oxygen reading will only show the "ultimate" CO2 (let's say 16% for oil) in this fuel rich area, based on the above. 3- A combustion analyzer that reads CO2 directly (by a sensor or chemically) may show a reading close to the "ultimate" or possibly lower in this fuel rich area. This is due to the unlikely chance that the "ultimate" can actually be achieved on most equipment, and once you go even richer on fuel, the chances are you are introducing more unburnt fuel into the process, causing dilution of the CO2 reading. In conclusion, I would now say that combustion analyzers that calculate CO2% from Oxygen% are not giving a meaningful CO2 reading in these fuel rich areas, and do not follow the rules of the charts we discussed. I would still maintain that the tech should have enough clues from other sources (smoke reading, CO reading, flame quality) not to be in these areas to begin with. I know this was a long thread that seemed to go nowhere for awhile, but I feel that I've learned something very valuable that I had not thought of before.
  • Firedragon Firedragon @ 5:33 PM
    Contact this user
    Glad to be of help!
  • Jim Davis Jim Davis @ 2:48 PM
    Contact this user
    CO Oil
    Mike the CO readings at Light-off and Shutdown are necessary to identify the actual problem and your meter may not pick these up. It is impingement of some sort. Your CO2 reading indicate you are close enough to proper fuel/air mixture, but your flue temperature would also be helpful. Could be a bad nozzle or an underfiring problem for starters.
  • John McArthur John McArthur @ 3:06 PM
    Contact this user
    oil burner CO
    the burner is underfired the boiler is a valiant f100-55 with a carlin e66 burner.the boiler is way too big.so in an effort to reduce short cycling. instead of being fired with a 1.75@ 45degree nozzle I have a 1.00@ 45 in there.The customer insist on a 100 degree water temp adding to my problems(temp runs on reset its about 140 degrees at zero outside] when I pull a smoke test the best i can get is abt a #1 and sometimes I get a yellow spot.the stack temp is abt 450
  • Jim Davis Jim Davis @ 3:23 PM
    Contact this user
    Underfiring is definitely a cause of high CO on some burners. Just had one recently and by using the same nozzle and increasing pump pressure the problem was eliminated. My second choice if that doesn't drop it below 100ppm would be to see if that Carlin can use a 60 degree nozzle. Hopefully you are using a solid nozzle. The last thing before you change the nozzle would be to adjust the drawer assembly but without being able to check light-off & shutdown this adjustment is more difficult.
  • John McArthur John McArthur @ 3:34 PM
    Contact this user
    nozzle
    I have an A nozzle in there because the customer said it was too loud that was a misguided effort on my part to quiet the thing down. Mr davis I need some info on how to get in touch with you about combustion training . thanks mike
  • Jim Davis Jim Davis @ 3:50 PM
    Contact this user
    Go to www.nationalcomfortinstitute.com for our information and phone number and call anytime.
  • jim sokolovic jim sokolovic @ 11:50 AM
    Contact this user
    Well, what type of instrument(s)...
    do you use? If the analyzer gives you an Oxygen reading, it has an Oxygen sensor. Does it also have a CO2 sensor that takes a direct reading? Other than chemical or infrared type analyzers, I am not familiar with any that read the CO2 directly. Maybe Jim Davis will rejoin this thread, I remember he had some disagreement with the theory behind the chart we are discussing, and knows the various analyzer methods of measurement well.
  • Dave Yates (PAH) Dave Yates (PAH) @ 1:17 PM
    Contact this user
    analyzers
    We have several Bacahrach and one UEI. They give readouts for net stack temp, CO, CO2 & O2. We've replaced (sent out for service and calibration) the O2 sensors several times. The Bacahrach does all on one screen & you can scroll through the UEI screens. Some day I hope to attend Jim's classes. To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Randy Randy @ 5:20 PM
    Contact this user
    normal CO readings
    we get range from a low of 6 to 50+/-. 300 sounds like incomplete combustion. We use Testo analyzers. Old burner?? Wrong nozzle??
  • Dave Mayer -3 Sons Heating Dave Mayer -3 Sons Heating @ 8:27 AM
    Contact this user
    CO
    Hey Mike: Normally I see levels oc CO ppm between 30-45 on properly running equipment. This is once they have achieved solid state running. I looked up the specs for the boiler burner combo you have. 1.50 x 45b is the norm according to Carlin. If you want to quiet it down etc. I would try a .85x45W Delavan nozzle make sure your pump is @150 psi. Where this boiler is rather long your flame might be "drifting off" as it does not entirely fill the chamber. There is nothing wrong with bringing several nozzles in the basement with you and "playing". This is where I learn the most. Shut off the cell phone so nobody can desturb you and enjoy. Just relax and enjoy your trade. Best of luck, Dave
  • Glenn Harrison Glenn Harrison @ 9:28 PM
    Contact this user
    Dave,
    According to all the electronic combustion analyzer brochures I have read, CO2 is a calculated number based on the O2 reading and the fuel your are measuring, which you must enter into the meter before measuring. I believe this is due to the extremely high cost of an electronic CO2 sensor.
  • Dave Yates (PAH) Dave Yates (PAH) @ 9:12 AM
    Contact this user
    if so
    then I'd expect to see zero CO2 on the fuel-rich side while CO should be greatly increased? Does this render the O2 reading obsolete? Maybe it's time to get the dumbells out of the archives, replenish the chemicals and go back to pumping! To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Glenn Harrison Glenn Harrison @ 12:24 PM
    Contact this user
    To the best ofmy knwledge...
    the calculation just allows the CO2 to go up as the O2 goes down, but the CO will go up so you know you've gone to far down on the O2. That is at least how my Testo works. Quite honestly, I don't have anything to do with the manufacturing of these units. Your best bet with any further questions is to contact Rudy Leatherman of Bacharach training @ rudy@eurekanet.com
  • Jim Davis Jim Davis @ 8:39 AM
    Contact this user
    CO2 & O2 exist on both sides of the combustion chart. Using bottles is like using a polaroid camera to film a movie and provide less accuracy because a flue has to be traverse to find the correct location to do the test in the first place and I don't think this was ever done with bottles.
  • jim sokolovic jim sokolovic @ 8:58 AM
    Contact this user
    Jim, can you tell us then...
    is the relationship of CO2 to Oxygen the same on both sides of the chart? When fuel rich - does the CO2 start going down and the Oxygen starts going back up, or stays at zero, or would you say "it depends"? Why can't we develope a very general chart that shows all this, if the one we now refer to is not complete or misleading? I know we touched on this before, but can you humor the topic a little more?
  • Jim Davis Jim Davis @ 11:30 AM
    Contact this user
    O2 & CO2
    Not sure if it is the same curve but I don't think it would be something that really needs to be setup because it is a dangerous place to be and to get out of as quick as possible. I have seen O2 readings on the Fuel Rich Side as high as 6%. As fuel input was reduced the O2 fell to 0% and then started back up the excess air side. At one time I had a CO meter that could read over 100,000ppm. By watching the CO drop from over 100,000ppm back to less than 100ppm as fuel was reduced and O2 dropped to 0% & then back up I was really amazed!
  • jim sokolovic jim sokolovic @ 11:42 AM
    Contact this user
    O.K. , so the Oxygen does not...
    stay at zero on the fuel rich side. Seems like that's good to realize for this discussion, and not be misled. "Get out as quick as possible" seems like good advice, too. Notice that I didn't offer to verify this myself!
  • Jim Davis Jim Davis @ 11:58 AM
    Contact this user
    Just for the record
    The 3 or 4 times I have seen this situation has always been on commercial equipment not residential.
  • N/A @ 12:12 PM
    Jim Solokovic
    I have a chart developed years back by Honeywell that goes on both sides of the excess air curve. What is your e-mail address I will send it off to you.
  • jim sokolovic jim sokolovic @ 12:45 PM
    Contact this user
    Timmie, can you...
    post it here, for everyone? I think there are enough others here that are interested in this. If not, my E-Mail is: jsokolovic@slantfin.com And to Jim Davis - Thanks for the info., our discussion is very general on relationships of readings - so commercial vs. residential should not be a factor?
  • jim sokolovic jim sokolovic @ 8:48 AM
    Contact this user
    O.K. Timmie, I received the chart...
    Still Oxygen is not shown on the fuel rich side, it stops at zero (at zero % excess air). CO is shown, but there is no question of where that goes here. Dave brought up the subject of what happens with the Oxygen reading as we go fuel rich, but we still have not settled on this fully?
  • Dave Yates (PAH) Dave Yates (PAH) @ 10:35 AM
    Contact this user
    and that's
    what I'm wondering about. With my old "dumb-bell" chemical set, I tested for O2 and CO2 separately. I was told way back when both of the Wilson brothers were alive and running our local Sid Harvey branch that without the O2 test, I wouldn't be performing my work correctly. In reading the Bacharach literature, their advice was confirmed & I spent the extra bucks for the O2 tester. Now comes electronic testing & a decided improvement in accuracy as well as eliminating the need to play with poisonous chemicals in order to refresh the dumb-bells. Looking at the chart, it appears CO mirrors, or nearly so, the O2 if you run over onto the fuel rich side and according to their posted literature, it's entirely possible to be on the wrong side without a sooty fire. So, I'm guessing the chemical CO2 tester would measure to either side, but the electronic units will only give a positive O2 and CO2 reading if on the excess air side of the psych chart? To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Firedragon Firedragon @ 1:21 PM
    Contact this user
    CO2 is CO2 and I heard
    Peter Cullen from Bacharach say that all summer (Carlin U). Peter said at every session (and I agree) that if the fluid and the instrument are dead nuts then there is no difference in accuracy from an electronic to a 'bottle'. The biggest difference is the need-for-speed, FACT! The last I heard the DOE was still requiring that final AFUE readings be done (for certification purposes) with an orsat which is a stationary 'bottle', but I've got enough to do and don't stay on top of lab-rat testing. There is no difference in CO2 and O2 reading in regards to excess air, excess air is excess air. I've plotted CO2/O2 in a lab and in the field before creating the infamous 'Lanthier Scale'. Although you may be on two sides of zero smoke (trace of smoke/fuel rich, or trace of zero air/rich) excess air will show by percentage of CO2/O2. The fastest way, IMO, to set a oilburner is with an ohmmeter first, backed up by a smoke tester and verified with an electronic tester. But, after you do enough tests you quickly realize that CO2/O2 testing is just that, verification of the chemistry taking place.
  • jim sokolovic jim sokolovic @ 2:52 PM
    Contact this user
    In our lab...
    we use an orsat to measure the CO2 during an AFUE certification test. Our Bacharach usually gives the exact same reading (to the nearest 0.1 %) as the orsat. If the Bacharach uses an Oxygen sensor to calculate a CO2, and we can see CO2 drop as we go further into a fuel rich mixture - then the Oxygen % must be also rising proportionally in this area. Why all the various charts neglect to show this, and no one seems to be able to 100 % verify this is the mystery here?
  • Firedragon Firedragon @ 3:12 PM
    Contact this user
    Regretfully Jim,
    I think there's too much assumption out there and so I'll jump in and tell you that many years ago a mechanical engineer who was also a chemist told me there was no difference. As smoke goes up CO2 goes up and O2 goes down, that's all there is to it, I really think that's all folks!
  • jim sokolovic jim sokolovic @ 3:30 PM
    Contact this user
    Grrrrrrroooooaaaaan!!!!!
    What am I missing here? How can so many people and these charts be in complete disagreement? Dave brings up something that I agree there should be a definitive answer to!
  • Dave Yates (PAH) Dave Yates (PAH) @ 5:42 PM
    Contact this user
    Thanks Jim
    I completely agree. Seems to me this should be a black or white issue with little fudge room - if any. If O2 hits zero as shown on the chart and we move over onto the fuel rich side, the CO rise pretty much mirrors O2 percentage wise. O2 should remain at zero until the fire extinguishes itself from a sufficient loss of combustion O2. I'd expect to see a sudden jump in O2 when the flame dies out. CO2 should also remain at zero, which only applies if CO2 is really being calculated on percentage of O2 in the electronic test instruments. To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Dave Yates (PAH) Dave Yates (PAH) @ 5:55 PM
    Contact this user
    Unless......
    The Oxygen % in the flue gases is being measured with CO too, which would allow for an increase of CO2 being "seen". But that begs the question (in my feeble brain) - wouldn't the percentage of Oxygen in CO be 1/2 that of O2 as excess air? If the instruments are designed to give CO2 percentages based upon O2 readings, wouldn't they be off the mark on the fuel rich side of the scale? To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jim sokolovic jim sokolovic @ 9:08 AM
    Contact this user
    Obviously, our discussion is leading...
    toward some "evil dark forest", that no one is supposed to speak of or enter. As I alluded to at the beginning of this thread, there should be certain immediate tell-tale signs that your adjustments are way off. That's why nobody can provide complete analysis of this area. If you ever go there again, and can gather all the readings we are so perplexed about, then please do reactivate this discussion - IF you do return, that is!
  • Firedragon Firedragon @ 4:01 PM
    Contact this user
    Sorry on my part!
  • N/A @ 5:44 PM
    I finally had some time to read this post
    and Jim S. I can say that in the past I have had some unusual occurences of being on the other side of the curve on some gas commercial large burner boilers. I deduced it was caused by a poor combustion chamber mix with what I call "tramp air" mixing at the point of testing. "Tramp air" is caused by openings and poor repairs to the boiler or flue area that allows air to be introduced after the combustion process. Those unusual air reading are rare and I do not believe they are combustion related. Jim Davis or George Lanthier may have some input toward that perhaps. I have never seen this in residentail applications. The chart I sent you supports the fact that on the left hand side of the curve there is no O2 only CO2 and CO. It is by the way very difficult to tell by eye at 8% CO2 when you are on the wrong side of the curve and it gets impossible at 9% and 10% on up toward ultimate CO2. That is why seeing a blue flame on gas is not the only answer you must test. It is also the case on conversions from coal and from oil to gas that boiler and furnace repairs and preperation before installing the power gas burner are a must. If there are leaks allowed then your readings are incorrect. It can be tested by closing up the air intakes on the burner and see if your O2 changes. I wish I had more time to discuss this at length.
  • Firedragon Firedragon @ 9:36 AM
    Contact this user
    Jim, although
    it wasn't done by many, it has been done with bottles and orsats! Learned how to do that in the USAF, but it's a lot easier with electronics, FACT!
  • Ken D. Ken D. @ 1:20 AM
    Contact this user
    Checking for CO
    An easy way to be sure you are on the propeer side of the curve is to check CO2. Close down air. CO2 should increase. If it decreases, you are on the wrong side. you can also open air and the CO2 should decrease. If it increases, you are on the wrong side. Hope this helps. Ken D. with a capital K.