    proper relay setup for 2 zones on 1 stat (6 Posts)

  • Big Ed Big Ed @ 10:16 AM
    Contact this user

    One Control

    Wire both zone valves to the thermostat with the largest load and reset the antisipater to the new current draw.....
  • Mike Pfluke Mike Pfluke @ 9:45 AM
    Contact this user

    I think I would splice a single thermostat wire into both zone valves so when the zone's thermostat called for heat both zone valves will open
  • Rob Rob @ 8:22 AM
    Contact this user

    If they're Taco 500 series, can a Honeywell CTIII handle what I think is 1.8A? (0.9A each)? I thought most stats can only handle up to about 1A. But I'm somewhat ignorant about this. thanks.
  • CC.Rob CC.Rob @ 9:40 AM
    Contact this user

    proper relay setup for 2 zones on 1 stat

    For hydraulic reasons, I need to make 2 smaller zones in a space that really only needs one stat. Assuming Taco zone valves and a standard 24V setup, what's the right way to do this? thanks.
  • STEVEN MARKS STEVEN MARKS @ 10:47 AM
    Contact this user

    Wire zone valve 1 to thermostat. Wire end switch of zone valve 1 to open zone valve 2. Wire end switch of zone valve 2 to start circulator.
  • Rob Rob @ 8:24 AM
    Contact this user

    sounds logical. Is this a common situation? thanks.
  •  