t-stat

@ December 29, 2012 11:21 PM in old Powers pneumatic thermostat question

I used to work on old peumatic systems and was a U.A, instructor,   if you give me the mod. number I may have the old cut sheet.  As everyone has said it is most likely a day/night t-stat,  look close for a smaller dial with 0-10 degree marking  this would be the degree of night setback, as Ed said dual prv's would change air press.to t-stats.  These types of systems are still being used in some old bldg's

F&T

@ December 29, 2012 12:47 PM in Float & Thermostatic Trap??

If you go to yahoo and look up F&T traps under Armstrong they have a good pictorial.    F&T traps gather condensate at the end of a line and release it back to the boiler,condensate pump or boiler feed tank by means of an internal float assy.  The T stands for temp.  the internal element releases unwanted air  The internal water seal prevents live steam from getting into the cond. line.  You can get a rebuild kit for this trap, you can check the temp. drop across the trap, if the outlet temp.is the same as the inlet than the trap is bad. Traps need to be maintained.  I would also clean out that wye strainer or replace it,   not sure where the rest of the piping goes.   I would cut out all that copper and repipe that whole thing in black pipe with a wye strainer ahead of the trap.

lwco

@ December 29, 2012 12:03 PM in lwco

Here is a picture of the inside of the bowl of a Mcdonnell Miller lwco that was not blown down or maintained

expansion tank

@ December 29, 2012 11:30 AM in Help! Problem with Burnham MPO temperature guage and pressure. Scratching my head??

Do you have a diaphram style tank, if so have you checked to see if it still has the air charge, you can use a tire guage, should be at least 12psig.   the other thing I would check is the fill valve, most have a small strainer you can remove and clean. If the fill valve is old and never cleaned the valve could be rusted and corroded internally, this could cause valve problems with internal valve parts causing valve to overfeed.   The fill valve is commonly overlooked.

rad. valves

@ December 28, 2012 1:54 PM in Air Vents v. Vacuum Breakers

I agree with all the pro's that have got back to you.    One other thing to check is the radiator valves.    In the past I have found rad. valves with cracked and deteriorated disk material ( disk is what closes against the valve seat )  what was happening was the valve was allowing steam into the radiator but not allowing condensate to drain back.   to check, shut off steam supply , disconnect the union on the valve, move the radiator and inspect the valve disc and seat.  the problem can also occur if the tenants are trying to use the valves as a  proportional control,  rad. valves must remain all the way open on 1 pipe systems. the tenants must be aware if they shut off a radiator. when the radiator is turned back on ( valve opened again )  there will be air and water in the radiator, you can expect banging and some spirting of air vent until water is allowed to drain back to system.

air flow

@ December 24, 2012 3:12 PM in help with measuring airflow

Go with a smaller range magnahelic, like a 0-.25 or 0-.5  remember if you think your looking for under 500 cfm your 2 inch mag is to big.  also are you measuring free area, if there is a grate, register or diffuser in the air stream you need to account for that, make a number of cross section readings and get an average reading.   In some cases registers etc can account for a 50% reduction in air flow readings.  There are also air flow meters you can attach to your volt/amp meter,  field peice makes a good one. the Trane air conditioning manual has a excellent chapter on air flow

Merry Christmas

@ December 24, 2012 11:38 AM in MERRY CHRISTMAS

Merry Christmas to you and your family  Steve

gas press.

@ December 23, 2012 2:34 PM in gas lines to boiler and other appliances

the outlet press. for natural gas  from most gas co. regulators is usually about 1/4 psig  (7 inches water column  w.c.)   regardless of the inlet press.  outlet press. over 1/2 psig can damage most diaphram gas valves

flue

@ December 23, 2012 11:30 AM in fluctuating draft with power vent + power gas

what about that single wall flue pipe ?

good product

@ December 22, 2012 10:23 PM in thankyou fan in a can.....

 have been using this fan on my commercial jobs for years   in some cases i have 2 . some basements just dont have enough space for gravity fed ducts for combustion/fresh air    Field controls also makes a good barometric damper

gas

@ December 22, 2012 8:54 PM in gas lines to boiler and other appliances

 Dont confuse psi with inches of water column ( w.c.)   most residential and small commercial bldgs have low press. gas service to the bldg regulator  ( 14 inches or 1/2 a pound )    5 psi could be considered medium press. gas, you could have med press.  you should contact your gas co. to get this info and have them sign off on this piping, looks a little sketchy to me.

cfm

@ December 22, 2012 11:21 AM in suppemental heat

As I stated carrier and other manufacts. use this cfm data.   I Installed , started up and serviced hvacr euip. for 38 yrs  I agree for system design do a heat load,  but in alot of cases when your on the job not in the office this rule of thumb gets you to a starting point.    I came from your fathers day   when a service man was expected to know all phases of this trade,  Lets appreciate what we have taught the younger guys,  without them this trade would be in trouble

piping

@ December 22, 2012 10:44 AM in need help reading the pressure gauge

I agree with Bob   should be repiped in blk pipe with cast iron fittings to allow pipe movement ( see swing joints )  the way it is now there will be pressure against the boiler sections causing problems

clocking

@ December 21, 2012 2:29 PM in Gas meter

Go on yahoo look up clocking a gas meter   good stuff

lwco

@ December 21, 2012 11:32 AM in LWCO Clogged

Lwco's need to be blown down weekly per  most manufact. ( Mcdonnell Miller ).  Strainer basket assy should be cleaned or replaced at least twice a year if not more often. Once a year I will completely take apart lwco and clean out bowl and flush out blow down valve.

combination

@ December 20, 2012 10:42 AM in auto feed system - necessary?

Many cities require redundant low water cutoffs on commercial boilers one of them being a lwco feed valve combination.  ex. ( mcdonnell miller # 51 ).  Yes a boiler could dry fire if any lwco is neglected.  Mc Miller recommends blowing down the lwco weekly.   I found when doing boiler P/M 's that if customer could do it themselves every 2 wks that was good.  I would clean or replace the strainer basket every 3 months and completely clean entire unit yearly especially the bowl float assy.

Merry Christmas

@ December 19, 2012 8:35 PM in Merry Christmas

Merry Christmas to all         remember John 3:16

power factor

@ December 19, 2012 8:28 PM in What watt!

My understanding is that  (power factor correction ) is not used in resistive loads, In a 3 phase suppl. heater circut we add the following      amps  = KW x 1000 divided by volts x 1.73.   On page 17 of the Ugly's book I believe they are talking about inductive, reactive loads.  (motors , transformers )   I always like to get several sets of eyes on all questions.

car ac

@ December 19, 2012 11:23 AM in Tips to repair Car Air Conditioners

Dont forget to change the cabin filter       It is fairly simple to get to on newer cars.   there are some good videos on you tube

vav

@ December 18, 2012 3:12 PM in Dual Duct VAV boxes - Inlet Pressure

Contact your local Trane rep. ask for  literature and request a I.O.M. (manual)  also on yahoo look up   HVAC units-Varitrane dual duct boxes.   you will need some training on this one.   may need  Rover/comm 4 software and Rover tool

pressure

@ December 17, 2012 2:26 PM in furnace firing issue

You need a minimum of 5 inches water column to inlet of most gas valves and 3.5 inches to burner on most  furnaces,  these setting can change if you have a 2 stage valve and on commercial burners. most diaphram style gas valves depend on this 5inch to 3.5 inch pressure drop to operate correctly.

Gas

@ December 17, 2012 1:05 PM in furnace firing issue

Have  a licensed Hvac contractor check it.   could be low gas press. you could start with your gas co.   alot of them dont charge to check your furnace.