rha

@ March 13, 2010 8:30 PM in relief valve

If the prv is piped at the expansion tank (point of no pressure change)  and the suction side of the pump then either tank is no good or its too small. This is assuming prv is not leaking by.

rha

@ March 13, 2010 8:30 PM in relief valve

If the prv is piped at the expansion tank (point of no pressure change)  and the suction side of the pump then either tank is no good or its too small. This is assuming prv is not leaking by.