Other side of heat exchanger

@ December 22, 2013 12:52 PM in Heat exchanger split after 4 years, misadjusted burner the cause?

Before replacing the furnace with any brand of furnace or fuel I would make sure the ductwork was properly sized, all vents open, and a clean filter always in the air path. Installing new equipment that will have high external static pressure and a temperature rise higher or lower than the appliance is rated for is just going to lead to another hx failure as in the past.

Air flow

@ December 21, 2013 3:21 PM in Heat exchanger split after 4 years, misadjusted burner the cause?

A major cause of heat exchanger failure is the air flow from the heat exchanger to the conditioned space. Too much airflow cools the heat exchanger too much and could cause condensation and rotting from rust. Not enough air flow causes the heat exchanger to overheat and crack.

A sign that this is the problem is a short cycling burner. The heat exchanger gets so hot that the limit control turns off the burner but the fan continues to deliver heat. Then the burner comes back on and continues this on/off cycling until the thermostat is satisfied. The high temp limit is there to protect your unit from overheating due to some failure to your unit. It isn't there to operate continually as part of normal operation.

Lp ga oven stopped baking.

@ December 21, 2013 3:06 PM in Lp ga oven stopped baking.

Last night we lost gas to oven while baking. Could see the hot surface igniter glowing but no flame. Found the wiring diagram and saw that the HSI was wired in series to the gas valve. Had 120 volts to igniter, 0 volts coming out the other side. Checked the resistance to the gas valve coil and had 1.3 ohms. Switched the broiler HSI to the bake and the wife finished baking the pie.

So it looks like the HSI is also working as a safety. Could someone please explain? I am only used to seeing them wired in parallel to a heating unit with a flame sensor as the safety.

What else could it be?

@ December 17, 2013 12:24 PM in williamson steam boiler not working? Need help

In your post you said that when you jumped out the thermostat wires it worked. Did you jump them out at the thermostat? If you did then the only problem it could be is the thermostat. Hopefully, all the changes you made since then have not added to the problem.

how old is furnace?

@ December 14, 2013 2:57 PM in 10 seconds of oil smell when oil furnace starts up

Some furnaces use temperature to start the fan but new ones are on a timer. I'm taking a wild guess that you have a oil spill, maybe in the blower cabinet that needs to be cleaned up. Could just be a small amount in the blower cabinet.

what brand ignitor?

@ December 13, 2013 3:20 PM in Beckett Burner irregular trips

If it's an old tar filled transformer then it could be getting weak. The new Carlin igniters have a bad habit of failing randomly. If you have a Carlin brand ignitor then I would recommend replacing it with either a Beckett or Allison brand igniter. These igniters are like light bulbs; once they fail they are not coming back. Makes troubleshooting the transformer easy.

Lost it's charge

@ December 13, 2013 3:15 PM in Boiler Pressure Spike while under heat

You could take the tank off and check the pressure with a tire gauge. It may have lost its air. Would recommend replacing it in this case. I've pumped a few back up but they just loose their air again in a few days.

Time

@ December 13, 2013 3:10 PM in HYDRO THERM BOILER PROBLEM

to call for service. Cost a couple of bucks but you will get your heat back full time.

expansion tank may be failing.

@ December 12, 2013 8:41 PM in Boiler pressure

Probably have spin-on expansion tank, or tanks to create an air cushion for the heated water. As the water in the system expands due to heat, the air behind the rubber diaphragm compresses and allows the water to enter the tank and keeps the boiler from flooding and dumping into the room. You need 1 psi of water pressure for every 2.31 feet the water has to travel up, plus 4 psi extra. That's what the fill valve should be set to  when cold. What ever pressure that comes out to should be the pressure your expansion tank is charged to when installed.

expansion tank may be failing.

@ December 12, 2013 8:41 PM in Boiler pressure

sorry, double posted.

make up air

@ December 12, 2013 8:30 PM in What is the definition of

is air brought in from the outside to supply enough oxygen for combustion.

Time for help

@ December 3, 2013 1:45 PM in Beckett 7505 120V GeniSys Control

Why don't you have the company that maintains your heating equipment wire this in for you? The diagram shows how it is done. If you don't completely understand this diagram you could do serious damage to the appliance.

variable speed circulators

@ November 29, 2013 9:44 PM in Maximizing efficiency of a mod con question

Here's a link to a pretty reasonable variable speed taco circulator. Set the Delta T and let her go...
http://www.pexsupply.com/Taco-007-VDTF5-007-Variable-Speed-Delta-T-Cast-Iron-Circulator-Pump-115V?gclid=CIG_74i-i7sCFaHm7AodKioABg

Time to play

@ November 21, 2013 9:34 AM in Ideal low and high temp for a biasi oil boiler

I have a similar setup except my indirect is a phase III. I would start by making sure the water heater has priority. Next, I would lower the indirect's aquastat to the lowest setting that will still deliver the needed amount of hot water. Lastly, I would lower the aquastat to a point that can still supply the needed temp for your tank to recover. My boiler aquastat is set at 160 degrees and the indirect's aquastat is set between low and medium. Have mine adjusted to be able to fill my bath tub.

Expansion tank

@ November 13, 2013 12:31 PM in Weil Mclain Ultra/DHW Issues again

Usually the old parts that you leave on a new install are the one's that will bring you back to the job. But that old expansion tank and the old Air scoop shouldn't create a problem. As long as you completely drain that expansion tank you should be good. If the tank only drops a small amount of water it may be completely waterlogged. You have to get all 15 gallons out of it or the problem will be right back.

If after completely draining the tank the relief valve starts to leak again in a short time you may have a leak between the domestic and boiler water tanks in your water heater. This can be checked if you have a drain valve between the water heater and the isolation valves of the hot and cold water going to the water heater. Just pick up a presure gauge with a drain connector, They sell them at hardware stores and home depot, connect to the drain valve and open that valve. Next note the pressure on the gauge. Next, shut the isolation valves to the tank's hot and cold water. Check the pressure gauge.

If, with those valves closed, you see the pressure drop, you know the high pressure water from the domestic side is leaking into the much lower pressure boiler side. If this is happening the water heater must be replaced.

Biasi

@ November 13, 2013 8:41 AM in Biasi boiler

Yes, this boiler is positive pressure. There are passageways between the combustion chamber and heat exchanger that may need to be cleaned. I've only cleaned them out once on a boiler that had clogged with soot. My Biasi is about nine years old and I have never needed to do this. I clean the combustion chamber every time I clean the boiler though

Strange

@ November 12, 2013 2:54 PM in Williamson Boiler Help!!

It seems strange to try and solve an electrical problem, resetting the burner, using plumbing parts.

Rel valve leaking

@ November 12, 2013 2:43 PM in Weil Mclain Ultra/DHW Issues again

There should be a domestic expansion tank on the unit. Modern water meters now come with back flow preventers. A back flow preventer can cause the pressure to triple from cold to hot.

Good advice

@ November 12, 2013 2:39 PM in Weil Mclain Ultra/DHW Issues again

Disconnecting the thermostat will prove wether it is the stat or not. I have the same water heater and keep it turned down almost completely. Would like to install a mixing valve when I have the time and the money. It is rare when I both though ;-)

CO

@ November 12, 2013 2:32 PM in combustion test

A cracked heat exchanger will effect the combustion gas by raising the o2 and lowering the co2. Just watched a webinar by RSES on this topic and they said that air from the air handler is going to push into the exchanger pushing CO up the chimney. Too much or too little oxygen will cause th CO to climb. If the chimney becomes blocked then the CO will find its way into the home.

Testy

@ November 12, 2013 12:32 PM in Quality of help on the Wall

I think most members are pretty generous about sharing their knowledge. I belong to another site that has a forum called ask our professionals. The most common reply to threads in this forum is "contact a professional."

They do not want to give away their knowlge for free or seeing anyone hurt themselves or others. Here it seem that, for the most part, we try and keep people from hurting themselves.

testo please

@ November 10, 2013 1:26 PM in combustion analyzer

I've owned a testo 325-1 digital CA for over 10 years and have had no real problems with it. If I was going to buy one today I would go with the testo 310. I'd like a 320 but the 310 would do everything I need done.

Here's a youtube link to a demonstration of these analyzers:
http://www.youtube.com/watch?v=JPTZH1Y9KlE