Tested

@ November 11, 2013 8:24 PM in Laars Endurance Help Advice What Next?

Ok tested the sensors and they are all in range. Based on what the laars techs say I either need a new circulator pump or the coil is scaled.

Went home to check it out and saw another f-4 on a call for hot from the laundry washer. Watched the boiler temp while wife was in the shower and noticed it start to climb hit 220 heard a clank and then it dropped back down but no f4. Not sure if this makes it sound like more of one than the other. Then on the next few fires it would climb to about 190-200 and then settle down no more clank/bang sound. Interested to hear what you think I should do next. Not looking forward to dropping another 200 plus time for a pump to figure out my coil is f'd. Got about 400 in parts and about 4-5 days of my time into it so far.

Also installed the flow restrictor too. Works great but still having soft lockout. Ugh!

Supply sensor?

@ November 11, 2013 11:13 AM in Laars Endurance Help Advice What Next?

So poking around and playing with the sensors I was able to replicate the F4 error by unplugging and plugging in the supply sensor. The other sensors threw different codes. Going to try and find a supply store open now and grab the mixing valve and the supply sensor and do them both. Hopefully it solves all the problems?

Thanks
Paul

Update

@ November 10, 2013 10:27 AM in Laars Endurance Help Advice What Next?

Not sure if this is related to the soft lockout that you guys pointed out as a possibility but over the last two days noticed two things

1. The bedroom upstairs furthest from the boiler is not getting as hot as even the adjacent room. I guess I'll bleed the system good to see if that helps.

2. Re soft lockout. I noticed when my wife was upstairs washing dishes the display started climbing as Normal and the. Spit an F4 code for a few seconds. Then hit like 229 and then back down.

In the manual it says an f4 code is to check the sensor plug? I guess my first question is which sensor plug? And could this be causing my issues that we thought was the mixing valve or not likely?

Thanks again guys. Sorry about all of this but you have given me hope I can fix this thing.

Paul

ugh

@ November 8, 2013 9:53 PM in Laars Endurance Help Advice What Next?

So I head home after work ready to isolate this problem thanks to all of you and what happens? Perfect shower. Perfect faucet. I don't get it.

The only differences compared to a normal day. I ran two faucets on hot and monitored temp to see if I could replicate before I shut off cold to test. Wouldn't work. So then headed up to the shower to try that. Normally my wife gives the baby a bath before showering but not tonight. In any case, hopped in the shower it was fantastic not a single drop in temp. Same for my wife. I just don't get this thing.

Not sure if this makes it lean more towards a mixing valve issue vs flow restrictor - but it certainly beats the hell out of me....sorry guys just need to vent no pun intended

thanks

ok

@ November 8, 2013 8:54 AM in Laars Endurance Help Advice What Next?

Just a little confused - if I shut off the cold and run the shower and it stays hot then that would mean the mixer is not working? Or is it because I shut off the cold and "self restricted" - it means I need the flow restrictor? Sorry for being a little dense here but want to understand how the cold in impacts one more than the other

thansk again

i do

@ November 8, 2013 8:41 AM in Laars Endurance Help Advice What Next?

Theres a valve right before the mixing valve on the cold in - I can shut that off - what should i do from there?

make sure i got it right

@ November 8, 2013 7:33 AM in Laars Endurance Help Advice What Next?

Firstly, Thank you all for your questions, suggestions and insight. It makes complete sense that so many turn to guys like you when they reach a dead end. Zman/Tom I think we are onto something!

So - the flow restrictor should be on the cold in to the mixing valve correct? I've rotated the pic of where it should be, sorry iphone for some reason made all the pics sideways.

The cold in line is at the rear in the pic. There is a shut off valve (which looks like it does in the picture in the manual) and then an elbow and the t for the valve itself. Could it be anywhere else? Or is it just missing???

Zman - with regard to the mixing valve - would you suggest a particular unit that is relatively cheap to try? The watts run about 30 bucks at home depot - but i do understand the get what you pay for. I guess if I'm cutting and sweating a flow restrictor in maybe I try a new mixing valve too?

thanks again guys
Paul

Pics

@ November 7, 2013 8:16 PM in Laars Endurance Help Advice What Next?

Hey guys. I think I'm getting what you need. If you need additional please let me know

possibly

@ November 7, 2013 2:58 PM in Laars Endurance Help Advice What Next?

when we first moved in - it was much worse. IT was random cold water spells but for much much longer periods of time and the only fix it seemed was to keep turning the faucet on and off until it magically got warm again, if at all. This issue seemed to dissipate after the heat started going on and the colder weather came (moved in sept 12)

After a few months of hearing the wife barking about her cold showers, I replaced the mixing valve guts and that seemed to help, eliminate the longer spells of cold water into maybe 30-45 second intervals and by increasing temp at the faucet it immediately would give more hot water (another weird problem) until it would ultimately get scalding hot when it did come back. Then it was the water flow switch that was suggested to change and then finally the exchanger. All provide marginally better performance for a few days but then back to the cycling of hot cold, which is where I am now

It has never had a problem getting hot or reaching a high temp. Just sustaining.

city

@ November 7, 2013 1:37 PM in Laars Endurance Help Advice What Next?

I am on city water - in terms of the pressure gauge on the unit itself - i have never seen it move, which is a good thing and is usually somwhere around 16 psi

IR

@ November 7, 2013 12:41 PM in Laars Endurance Help Advice What Next?

would an infrared work? I don't have a clamp on - I assume once I post the pics you will let me know where I should focus my readings?

fishing

@ November 7, 2013 10:26 AM in Laars Endurance Help Advice What Next?

Hey Guys,

Sorry I used that old saying - fish or cut bait. I guess I've been fishing too much!

I will get some pics as soon as I get home tonight and post them. Other than this issue - we haven't really had any problems getting the house to temp on the t-stat, so I assume that its isolated to the DHW side?

Some more info on the mixing valve - I had two plumbers take a look at this and they both said that the mixing valve appears to be working properly. I replaced the "guts" to see if it would help, didn't sweat a brand new one in. Basically asked the plumbers to do it and they said it would be a waste of money because they think it works just fine.

I'd say being in the northeast (RI) the water is a little hard and I've seen evidence of the buildup on both the mixing valve and water flow switch. Not so much the heat exchanger, it actually looked ok on the inside.

Any other pics you think that would help? I will try my best. Thanks again!

Laars Endurance Help Advice What Next?

@ November 6, 2013 10:16 PM in Laars Endurance Help Advice What Next?

HI All,

I have a Laars EBP 110 endurance combo unit. It is about 6-7 years old. Just moved into the house about a year ago and noticed issues in the showers or faucets and depending on the time of year, for some reason, summer being the worst, we would get intermittent cool showers. Got to a point where we could time when the cold/cool water would hit. Would run in like 30 second cycles.

Fast forward through a couple plumber calls, Laars tech calls and some DIY googling and I am at my wits end. I've replaced the following

1. Mixing Valve (watts 70a)
2. Water Flow Switch (as recommended)
3. Heat Exchanger (what a pain in the ass that was)

After all these tweaks, it would get marginally better but then back to cycling hot/cold water. The unit has no problem getting up to temp. Firing up on demand. Delivering hot water in a reasonable period of time. It just can't sustain it for a 5-10 minute shower with no other hot water running. I've tested through all of the showers and faucets in the house with thermometer and can record up to a 15-20 degree swing in temp without touching the faucet itself. The last plumber said it was time to cut bait.

Not sure where else to turn but to a new unit - not sure what's out there that won't break the bank - a direct replacement runs about 2500 bucks really not looking forward to replacing it with the same.....Maybe the folks from Laars who post here from time to time might help?

thanks