Weil

@ May 1, 2004 9:21 PM in Weil Mclain Ultra boiler noise

Had three Ultra 230? on LP with the same thing I tried about everything testing, testing, finaly found the pressure problem in the gas. The LP company had a heater on the tank ( liguid out of tank ) the reguator when the total load came on 3,600,000 btus would stick and give me 2 " on the boilers after a shut down. Sun then would heat the regulator up and be fine. Took me three weeks , rep, and salesman trips to get to the problem. cheak the pressure at the boiler. I left a water mon. on it to finaly fine it.